    Default State Machine Viewer - missing transition

    Hello every one,
    can you explain me why I get different state transition diagram from relatively the same VHDL?
    Here is the code:
    1)
    if rx_bit_index < 7 then
    rx_bit_index <= rx_bit_index + 1;
    rx_state <= s_rx_data_bits;
    else
    rx_bit_index <= 0;
    rx_state <= s_rx_stop_bit;
    end if;
    2)
    if rx_bit_index = 7 then
    rx_bit_index <= 0;
    rx_state <= s_rx_stop_bit;
    else
    rx_bit_index <= rx_bit_index + 1;
    rx_state <= s_rx_data_bits;
    end if;
    and here the state transition:
    New Bitmap Image1 - Copy.bmp
    New Bitmap Image1.bmp

    Regards,
    Emil

  2. #2
    Join Date
    Feb 2018
    Posts
    75
    Rep Power
    1

    Default Re: State Machine Viewer - missing transition

    Hi Emil,
    Quote Originally Posted by lz5za View Post
    can you explain me why I get different state transition diagram from relatively the same VHDL?
    Here VHDL codes aren`t same, It leads the different state transition diagram,
    1) rx_bit_index <= 0; In all cases except when rx_bit_index has value ranges from 0 to 6;
    2) rx_bit_index <= 0; only when if rx_bit_index = 7

    Let me know if this has helped resolve the issue you are facing or if you need any further assistance.

    Best Regards
    Vikas Jathar
    Intel Customer Support Engineering
    (Under Contract to Intel)

  3. #3
    Join Date
    Mar 2017
    Location
    Sofia
    Posts
    5
    Rep Power
    1

    Default Re: State Machine Viewer - missing transition

    Hi Vikas,
    thank you for the quick answer.

    May be I didn't explain enough what I am doing

    the two IFs are within a CASE within a PROCESS

    So:

    p_UART_RX : process(CLOCK)
    begin
    if rising_edge(CLOCK) then

    case rx_state is
    when...........................

    --FIRST VARIANT
    when s_rx_data_bits =>
    if rx_clk_count < g_CLKS_PER_BIT-1 then
    rx_clk_count <= rx_clk_count + 1;
    rx_state <= s_rx_data_bits;
    rx_smp_tick <= '0';

    else
    rx_clk_count <= 0;
    rx_data <= rx_stable & rx_data(7 downto 1); -- LSB first
    --rx_data(rx_bit_index) <= rx_stable; -- Wait g_CLKS_PEBIT-1 clock cycles to sample serial data
    rx_smp_tick <= '1';

    if rx_bit_index = 7 then -- !!!
    rx_bit_index <= 0;
    rx_state <= s_rx_stop_bit;
    else
    rx_bit_index <= rx_bit_index + 1;
    rx_state <= s_rx_data_bits;
    end if;
    end if;

    --SECOND VARIANT
    when s_rx_data_bits =>
    if rx_clk_count < g_CLKS_PER_BIT-1 then
    rx_clk_count <= rx_clk_count + 1;
    rx_state <= s_rx_data_bits;
    rx_smp_tick <= '0';

    else
    rx_clk_count <= 0;
    rx_data <= rx_stable & rx_data(7 downto 1); -- LSB first
    --rx_data(rx_bit_index) <= rx_stable; -- Wait g_CLKS_PEBIT-1 clock cycles to sample serial data
    rx_smp_tick <= '1';

    if rx_bit_index < 7 then --THE DIFFERENCE IS HERE
    rx_bit_index <= rx_bit_index + 1;
    rx_state <= s_rx_data_bits;
    else
    rx_bit_index <= 0;
    rx_state <= s_rx_stop_bit;
    end if;
    end if;
    when...........................
    when others => rx_state <= s_rx_idle;


    end case;

    end if;
    end process p_UART_RX;

    THE both variant have the same behavior but in the state machine viewer the transition stroke are missing for the second, and I do not understand why?
    Else the both code work correctly and a signal tab show correct transitions

    Regards,
    Emil

  4. #4
    Join Date
    Mar 2017
    Location
    Sofia
    Posts
    5
    Rep Power
    1

    Default Re: State Machine Viewer - missing transition

    Hi Vikas,
    not realy.
    may be I didn't explained correctly the case.

    The both IFs are with in a clocked process within a case. The IFs are just the transition condition to the next state, and they are equivalent: when 7 -> transition else count. I can describe as count if < 7 else transition or count and if = 7 transition.
    In the simulation it is corect in real test too but the state machine viewer do not like the "<" sign

    Regards,
    Emil

  5. #5
    Tricky is offline Moderator **Forum Master**
    Join Date
    Oct 2008
    Posts
    6,031
    Rep Power
    1

    Default Re: State Machine Viewer - missing transition

    The main question is does this code work as you expected, for both variants? Have you got a testbench? have you simulated and got the correct result? have you tested it on FPGA and both cases work?

    The code IS different. While this snippet does look functionally similar, they are actually logically different.
    For example - the first one has logic to only change state when rx_bit_index is a single value - 7. The second code can change state when rx_bit_index is any value greater than 6 (depending on the declaration of rx_bit_index, this will be a minimum of 9 values, 7-15)
    Because of this, Quartus has decided there are optimisations that can be made. But because you only show a small snippet of code, not all of it in context, and you dont say if it works, its impossible to say why Quartus has changed the state diagram. If the code doesnt work, then this will be the reason for the state difference.

  6. #6
    Join Date
    Mar 2017
    Location
    Sofia
    Posts
    5
    Rep Power
    1

    Default Re: State Machine Viewer - missing transition

    Yes, you are right saying that in the second variant the state change at any value greater than 7. But the first value at which there is a transition is 7, and Quartus do not show this. Why?
    Else the declaration of rx_bit_index is
    signal rx_bit_index : integer range 0 to 7 := 0;
    And the index is set to 0 after reaching 7.
    I mentioned that "In the simulation it is corect in real test too" It work (the both codes) on MAX II device and is correctly behaving in ModelSim
    Regards,
    Emil

  7. #7
    Join Date
    Dec 2007
    Location
    Bochum Germany
    Posts
    6,319
    Rep Power
    1

    Default Re: State Machine Viewer - missing transition

    I believe both variants are functionally equivalent. I don't see any ambiguity (at least in the posted code snippet). I presume there are neither state overrides below the case construct.

    The fact that the state machine viewer misses the state transition to s_rx_stop_bit, which apparently occurs both in simulation and synthesized code, seems to indicate a bug.

  8. #8
    Join Date
    Mar 2017
    Location
    Sofia
    Posts
    5
    Rep Power
    1

    Default Re: State Machine Viewer - missing transition

    Quote Originally Posted by FvM View Post
    ..... seems to indicate a bug.
    That is what I supposed. And it is only in the visualization in the viewer.
    Thank you for the answers.
    Regards,
    Emil

  9. #9
    Join Date
    Feb 2018
    Posts
    75
    Rep Power
    1

    Default Re: State Machine Viewer - missing transition

    Hi Emil,
    Quote Originally Posted by lz5za View Post
    The both IFs are with in a clocked process within a case. The IFs are just the transition condition to the next state, and they are equivalent: when 7 -> transition else count. I can describe as count if < 7 else transition or count and if = 7 transition.
    In the simulation it is corect in real test too but the state machine viewer do not like the "<" sign
    Can you check with either
    if rx_bit_index <= 6 then --THE DIFFERENCE IS HERE
    OR
    signal rx_bit_index : integer range 0 to 8 := 0;
    if rx_bit_index < 7 then --THE DIFFERENCE IS HERE


    I am able to see the state transition to s_rx_stop_bit in the state machine viewer.
    Check Screenshot.

    Let me know if this has helped resolve the issue you are facing or if you need any further assistance.

    Best Regards
    Vikas Jathar
    Intel Customer Support Engineering
    (Under Contract to Intel)
    Attached Images Attached Images

Similar Threads

  1. State Machine Viewer
    By roger8144 in forum Quartus II and EDA Tools Discussion
    Replies: 1
    Last Post: March 29th, 2017, 11:25 AM
  2. Get result of State Machine Viewer
    By charlestsai in forum Quartus II and EDA Tools Discussion
    Replies: 3
    Last Post: June 11th, 2013, 04:50 AM
  3. State Machine Viewer State Machine Missing
    By KnightRider123 in forum General Altera Discussion
    Replies: 0
    Last Post: September 24th, 2012, 12:49 AM
  4. Why I cannot see the my state machine in the statemachine viewer?
    By ertss in forum Quartus II and EDA Tools Discussion
    Replies: 1
    Last Post: January 10th, 2011, 02:49 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •